New Part L Revision re Applications lodged after Nov 2011
- This topic has 16 replies, 4 voices, and was last updated 12 years, 10 months ago by Anonymous.
-
AuthorPosts
-
-
November 20, 2011 at 1:03 pm #711449AnonymousInactive
I cannot help feel that this Part L has been let run away with itself with no real assessment of its implications.
Far too much of the billing and cooing on Construct Ireland seems to be without critical comment – nothing is THAT good.
===========================================================================================================
News
REVISED PART L – Important Message from the RIAI Practice DirectorPosted: Friday, November 11, 2011
RIAI Practice Director, Joe Miller has issued an important message to RIAI Members on the forthcoming revised Part L of the Building Regulations.
“I cannot stress enough how important it is to understand the forthcoming changes in Part L 2011 of the Building Regulations to the way we design domestic dwellings. As you will see below, Part L 2011 will come into force in about 3 weeks, on the 1st December 2011; the transitional period ends on the 30th November 2011. Unless a planning application is made by that date, compliance will be required with Part L 2011 for planning applications on and after 1st December 2011.
Compliance with Part L requirement is quite onerous, both in terms of design and construction. The Part L Road Show programme will analyse the changes that are relevant in the new Part L 2011 and comparisons will be drawn between them and the current Part L requirements. The case studies, which form the latter part of the Road Show, will demonstrate how compliance can be achieved at the design stage, in some cases with the greatest difficulty, for the semi-detached house; an apartment building; an extension to an existing dwelling and an historic building with an exempted development to the rear. We announce the RIAI Road Show below and urge as many of the RIAI members, as possible, to attend.”
Download Technical Guidance Document Part L – Conservation of Fuel & Energy – Dwellings (2011)
http://www.environ.ie/en/Publications/DevelopmentandHousing/BuildingStandards/FileDownLoad,27316,en.pdfThe RIAI has arranged an RIAI Skillnet CPD Road Show on the New Part L with dates, costs and location below:
View the event programme
Download the booking form
Dates:
Dublin on Thursday 24 November 2011 – (9.15am-1.30pm)
Galway on Tuesday 29 November 2011 – (1pm-5.15pm)
Cork on Thursday 1 December 2011 – (1pm-5.15pm)Tutors: Members of the RIAI Sustainability Taskforce
Cost: RIAI practices €95 (price includes RIAI Skillnet funding as applicable)
RIAI member* €105 (price includes RIAI Skillnet funding as applicable)
Non-RIAI member €160
For further information contact:Teresa Harte, RIAI, 8 Merrion Square, Dublin 2. Tel (01) 676 1703 Fax (01) 661 0948 e-mail: tharte@riai.ie
-
November 20, 2011 at 1:39 pm #817419AnonymousInactive
The URL of the page on the RIAI website from which the above notifation is take is –
-
November 21, 2011 at 5:50 pm #817420AnonymousInactive
@onq wrote:
I cannot help feel that this Part L has been let run away with itself with no real assessment of its implications.
Far too much of the billing and cooing on Construct Ireland seems to be without critical comment – nothing is THAT good.
a working understanding of the current part L makes it much easier to understand what is coming down the tracks.
Basicaly, houses are going to go from 40% more efficient than the baseline standard, to 60% more efficient.this is going to to put much more focus onto the dark art of thermal bridge calculations, energy demand calculations and air tightness detailing.
the days of worrying about elemental u values are well behind us.
-
November 21, 2011 at 9:15 pm #817421AnonymousInactive
I don’t disagree with anything you say Henno, but there is a wider picture than the aspirations of people who seem to centre on thermal efficiency and sealing.
People I have spoken to have agreed that the sealing standard is pointlessly high may be leading us to serious ill bronchial ill health.
Sensationalist as this sounds it is clear that we have assimilated aspects of commercial design with none of the safeguards.MVHR is a cut down version of full air conditioning but with none of the fire prevention measures.
In addition the hazard is higher in the house which has potentially a 100% sleeping occupancy.This is greater than even a hospital or nursing home where there are alert staff on call.
Branching ducts can allow for the regulated transfer of old smoke and fumes transfer.Ducts containing water and deposits can be a breeding ground for bacteria.
This can create conditions for legionella to grow outside of the hot tub.
http://www.cmse.ie/blog/legionella-in-ireland/I don’t think we’ve thought this all through for Irish conditions.
-
November 22, 2011 at 8:44 am #817422AnonymousInactive
To compound matters, we live in a wet climate, rather than a central European dry climate. Without climatic control on venting systems moist air is delivered from the outside directly to the middle of the house.
Also please note that the mean temperature due to Global Warming is climbing. During warmer spells such as at the moment or more particularly during the summer what happens when the house overheats? You open the window thus bypassing the air tightness requirements.
Air tightness is a black box physics experiment that works when you do not include the variable; people.
-
November 22, 2011 at 8:51 am #817423AnonymousInactive
Importance of Ventilation
http://www.humidex.ca/humidexwp/wp-content/uploads/2010/12/ASHRAE-NOV-2010-IAQ-in-AirTight-Homes.pdf
“What we must always remember is that buildings are for people, and thus health must trump energy. When concerns for energy costs exist because of cold or hot climatic conditions, the response should not be to reduce the outdoor air ventilation, but rather to pursue energy conservation measures. Similarly, when concerns are present for high outdoor air contaminant concentrations, then air cleaning measures should be pursued. The home ventilation mantra remains; build tight, but ventilate
right.” -
November 22, 2011 at 11:05 am #817424AnonymousInactive
This is what it all comes back to Shadow – the climate of thsi country and what is reasonable
This started with a concern about saving fuel and reducing the carbon footprint.
Then it progressed through a reasonable level of insulation.
Then it went mad with sealing and ventilation.
Ventilation that isn’t entirely passive requires energy to drive the pumps.
Pumps need to be replaced every seven to ten years at considerable cost and expense.
Someone needs to to a proper accounting of costs and savings overall for the benefit of the consumer – us!
-
November 22, 2011 at 11:11 am #817425AnonymousInactive
Here’s a great detail – a construction stuffed full of insulation – http://t.co/v8d1Hcx1
100 Interweb points for guessing where the interstitial condensation is most likely to occur.
Hint condensation that occurs within the insulation can reduce its effectiveness.
There is a theoretical point beyond which insulation cannot go.
Thus the emphasis on sealing, but its not understood.
Unless you seal the sandwich perfectly it starts to get wet internally.
Realizing this was impossible the powers that be suggested controlling “air quality”.
People get confused between oxygen levels and humidity levels, both of which need control for “good air”.
-
November 25, 2011 at 5:30 pm #817426AnonymousInactive
@onq wrote:
MVHR is a cut down version of full air conditioning but with none of the fire prevention measures.
In addition the hazard is higher in the house which has potentially a 100% sleeping occupancy.
.on this issue i completely agree with you. all my specifications for hrv include smoke protection collars for all ducting when passing through floors / walls. Also, connection to fire detection system is a must to allow for full ‘shut down’ in case of fire.
These were issues brough to the attention of BRAB, but no mention in Part L 2011. We can only hope for main stream provision in an altered Part B…. but regardless we as designers must provide the best spec we can .@onq wrote:
Ducts containing water and deposits can be a breeding ground for bacteria.
This can create conditions for legionella to grow outside of the hot tub.
http://www.cmse.ie/blog/legionella-in-ireland/I don’t think we’ve thought this all through for Irish conditions.
in this i dont agree. again, care needs to be taken with the specification ie never flexible ducting!! and always locate the system within the heated insulation envelope.
The exhaust air never actually mixes with the incoming air, therefore there is no influx of contaminated air back into the house… if anything the hrv system works as an efficient exhaust vent system. the temps required to allow legionella wont be reached in the exhaust system as long as common sense prevails with condensation issues. -
November 25, 2011 at 5:38 pm #817427AnonymousInactive
@onq wrote:
Here’s a great detail – a construction stuffed full of insulation – http://t.co/v8d1Hcx1
100 Interweb points for guessing where the interstitial condensation is most likely to occur.
Hint condensation that occurs within the insulation can reduce its effectiveness.
There is a theoretical point beyond which insulation cannot go.
Thus the emphasis on sealing, but its not understood.
Unless you seal the sandwich perfectly it starts to get wet internally.
Realizing this was impossible the powers that be suggested controlling “air quality”.
People get confused between oxygen levels and humidity levels, both of which need control for “good air”.
you picked a very bad example to make your point
that detail, while not perfect… is specifially designed to reduce thermal bridging as much as possible. the roof construction is created as a warm roof type (see gutex wood fibre) with a breathable felt over. In this construction vapour will only condense into liquid over the felt and into a ventilation layer and exhausted away. the dew point in this detail occurs outside the insulation layer
condensation in the wall construction will occur at the cold face of the cavity insulation, and is allowed to exhaust through the external blockwork.Investigations into the condensation point can be done with software such as wufi, which gives a dynamic rather than static view of where condensation will occur.
-
November 25, 2011 at 8:26 pm #817428AnonymousInactive
Henno,
How can you be so sure where the dewpoint will fall?
It is a function mapping the reduction in temperature against humidity.
The more insulation there is the greater the chance that dewpoint will occur withing the insulation.
I’m not interested in where it *can* occur, but where it will occur with higher insulation for a wide range of conditions.
-
November 25, 2011 at 8:30 pm #817429AnonymousInactive
@henno wrote:
in this i dont agree.
again, care needs to be taken with the specification ie never flexible ducting!! and always locate the system within the heated insulation envelope.
The exhaust air never actually mixes with the incoming air, therefore there is no influx of contaminated air back into the house… if anything the hrv system works as an efficient exhaust vent system. the temps required to allow legionella wont be reached in the exhaust system as long as common sense prevails with condensation issues.The temp will be exceeded in the input system, with temperature losses from the travel down the pipe and 16-18 degrees required its well within the legionella comfort zone, and legionella is only one possible biological outcome when you’re in the 18-24 degree range: that’s where a lot of moulds thrive as well.
-
November 30, 2011 at 2:27 pm #817430AnonymousInactive
thats why they have condensors fitted in the heat exchanger.
-
December 1, 2011 at 2:26 pm #817431AnonymousInactive
Sounds interesting. What do you think they do – Inlet and Outlet? And to the carbon footprint?
-
December 2, 2011 at 3:05 pm #817432AnonymousInactive
are you seriously asking me what do i think a “condensor” does? ……….. :wtf:
-
December 3, 2011 at 7:25 pm #817433AnonymousInactive
Just as a matter of interest;
Post occupancy, what happens when the owner/occupier puts up shelves, pictures, flat TVs, curtains or new lights on various walls. Surely the perfectly assmbled, detailed and airtight proofed environment is compromised. Worse still because of the semi pressurised environment any compromise will focus the movement of vapour to a critically vulnerable location in the wall system.
-
December 6, 2011 at 10:00 pm #817434AnonymousInactive
@shadow wrote:
Just as a matter of interest;
Post occupancy, what happens when the owner/occupier puts up shelves, pictures, flat TVs, curtains or new lights on various walls. Surely the perfectly assmbled, detailed and airtight proofed environment is compromised. Worse still because of the semi pressurised environment any compromise will focus the movement of vapour to a critically vulnerable location in the wall system.
this isnt so much an issue with a masonry house, as the plaster layer is the airtightness layer. simple eduction to the occupier as to how best finish drill holes would suffice ie plenty of caulk
in a TF house it can be an issue but one that should be designed to minimise any risk of puncturing the air tighness membrane. this is usually done by incorporating a service cavity of say 75 – 100 mm between the inner face an dthe timber frame. The air tightness membrane is affixed to the frame so there is a depth protection by the service cavity. Also any good TF spec should include a strong OSB inner lining prior to plaster boarding. This can easily act as a ground for most domestic applications. In cases where there is doubt, the spec should be altered to include cementious board.
basically, fore sight and education is required. it would be a very foolish occupier to pay extra for an air tightness strategy and MHRV and then not know how it affects the dwelling.
as for the pressurisation point, i think you put way too much credit into the ability of a HRv system to create pressure differentials.
A simply day like today where it is say 20 degrees internal climate and 4 degress external would create a vast greater pressure differential than any HRV system could. The investigation of condensation issues should be carried out regardless of any percieved differential anyway. Most problems actually occur when there is negative pressure in summer times when its warmer outside thus creating a situation where condensate moisture is drawn back into the building rather than being allowed to exhaust outward. The use of non breathable materials along the inner face is what causes problems in this situation eg drylining with polythene DPMs etc.
-
-